Home Repair Forum
Go Back   Home Repair Forum > Indoor Home Repair > Plumbing
Register Chat FAQ Members List Calendar Search Today's Posts Mark Forums Read

Reply
 
LinkBack Thread Tools Display Modes
  #11 (permalink)  
Old 04-06-2008, 07:26 PM
LazyPup's Avatar
Master Journeyman
 
Join Date: Apr 2004
Location: Sharon, PA, USA.
Posts: 2,133
LazyPup is on a distinguished road
The Bosch Aquastar125 series included the 125NG (natural gas) and the 125LP (liquefied petroleum).

Although the 125x series is now discontinued I did manage to find a downloadable copy of the installation manual in PDF format at:

Tankless Water Heaters from Bosch, Takagi Flash TKJr, TK3, T-M1 - fueled by Gas & Propane and Powerstream, PowerStar and Ariston Electric Tankless and Electric Mini-Tank Hot WaterHeaters and On Demand Water Heaters

In reviewing the manual I came across a number of details that would warrant attention.

PERFORMANCE:
The AQ125xng is rated for 3.7gpm @ a 45degF rise. Assuming you desire the maximum code rated hot water temp of 125degF the incoming cold water would have to be 85degF to achieve the maximum flow rate. This might be practical in mid summer in the Sunbelt where the water lines are buried rather shallow and the soil is heated by solar energy, however, in Northern climates where the water lines are buried a minimum of 6” below the average frost depth in mid summer we can expect the cold water to come in at the earths natural geothermal temperature of 50-55degF. On the other hand, in mid winter we can expect the incoming cold water to range in the 35 to 40degF range. With an incoming temperature of 35degF and a hot water calling temperature of 125 we have a 90degF differential, and at 90degF differential the AQ125xng is rated for a maximum flow rate of 1.8gpm. This may be okay for those such as myself who enjoy a moderate shower at around 90degF but for those who enjoy a very hot shower 1.8gpm will not meet the needs of even a water saver shower head (2.5gpm), not to mention the cold spike you that would occur if someone were to start the dishwasher, laundry or even wash their hands at a lavatory in another bathroom.

VENTING: (See Local codes)
The venting must be in compliance with the national gas code and all local codes for a category 1 appliance rated at 116,000btu.

Requires Type B (double wall) vent pipe.

The minimum vent height must be 6’ provided there are no elbows and the point of termination must be 2’ above any obstruction within a 10’ radius.

When a horizontal run of vent is required, the vent must have as much vertical rise as possible (minimum 12”) before turning horizontal.

All horizontal venting must have a ¼” per foot pitch upwards towards the exterior stack.

The maximum length of a horizontal run may not exceed 100% of the total vertical rise. (When a horizontal pipe is used to exit the structure, the length of the vertical riser stack on the exterior must be equal to or longer than the horizontal length.)

The vertical riser must terminate at a point at least 2’ higher than any obstruction within a 10’ radius of the point of termination and the top of the riser must be equipped with an approved weather cap.

GAS SUPPLY (PIPE SIZE):
The AQ125xng may be supplied by a ½” black iron pipe, provided the maximum developed length of the pipe from the gas meter to the water heater inlet does not exceed 10’. If the maximum developed length of pipe from the meter to the water heater is greater than 10’ but equal to or less than 40’ it may be supplied with a ¾” gas line and if the maximum developed length is greater than 40’ but less than 150’ it requires a 1” line.

This is assuming that the AQ125x water heater is the only appliance attached to the gas line.

When we have multiple appliances on a common gas line we must first total the BTU requirements of all gas appliances, then convert the BTU requirement to cubic feet of gas per hour.

By example; let us assume a house that has a gas furnace (150,000btu), A freestanding gas range in the kitchen (35,000btu), a gas laundry dryer (35,000btu) and the AQ125xng (116,000btu).

The total BTU requirement for the structure is then 336,000btu. The codes state that we are to then contact the local gas supplier and get the actual BTU/cu.ft value of the gas, but in instances when that information is not available we may use the average value of 1100btu/cu.ft

Dividing the total BTU requirement (336,000btu) by 1,100btu/cu.ft we get 305cu.ft

We must then compute the total developed length of pipe from the gas meter to the furthest appliance.

NOTE: The total developed length of the pipe is the actual length of the pipe including rises and drops plus the fitting insertion losses, which are expressed in lengths of pipe. By example, a ½” black iron pipe 90 elbow has an insertion loss equal to .8’ (9.5”) of pipe.

For illustration let us assume that the total developed length to the furthest fixture is 70’. Per IRC table T2413.4(1), With a load of 305cu.ft and an overall length of 70’ we would need to begin at the gas meter with a 1” pipe and continue running 1” until the first appliance tee’s off the line. From that tee we would deduct the BTU rating of that appliance, then compute the balance to cu.ft as before and determine the maximum developed length from that tee to the last fixture to determine the size of pipe from that tee to the next fixture tee. We then repeat the process again and again until we have sized all the pipes by the Cu.ft table.

MAINTENANCE REQUIREMENTS
Per instructions in the AQ125xng installation manual we must inspect the Main burner, Pilot Assembly, Water screen assembly, and vent assembly annually. The water valve must be lubricated at least once every 2 years and the water valve must be rebuilt one every 3-5years,
Reply With Quote
  #12 (permalink)  
Old 04-06-2008, 09:27 PM
Master Handyman
 
Join Date: Apr 2006
Posts: 206
DKAudio is on a distinguished road
Thanks for the info, I did not take into account the starting temp of the water. My wife takes very hot showers/baths, maybe I will hold off on this one.

I do plan on getting a tankless eventually. I really want to get the water heater away from the center of our laundry area, it is pretty wasteful of real estate.

Like I mentioned, right now we have a 1980 40 gallon that cannot keep up very well. It does ok except for when my wife uses the shower, then I have to wait a little before I can.

Thanks again.
Reply With Quote
  #13 (permalink)  
Old 04-06-2008, 10:58 PM
LazyPup's Avatar
Master Journeyman
 
Join Date: Apr 2004
Location: Sharon, PA, USA.
Posts: 2,133
LazyPup is on a distinguished road
Do you have a basement?
Reply With Quote
  #14 (permalink)  
Old 04-08-2008, 01:31 PM
Master Handyman
 
Join Date: Apr 2006
Posts: 206
DKAudio is on a distinguished road
Yes, not full 8' ceilings though. Probably around 7' or under to the joists.
Reply With Quote
  #15 (permalink)  
Old 04-14-2008, 10:32 PM
New Member
 
Join Date: Jun 2007
Posts: 3
travisdecpn is on a distinguished road
I know I may be coming in a little late on this one, but if you are going to mount a tankless unit in a basement, it needs to be a direct-vent model to pass code (and more importantly work correctly). You would be much better off to mount the unit on an exterior wall and use and outdoor unit. It's a little more involved since you have to move your piping and provide a 120V outlet, but you'll save a ton of money on venting materials.

As far as pipe size goes, the diameter required is determined by the distance from the source (most likely as gas meter for residential units) and the BTU demand of the unit. Most tankless heaters for a whole house will be in the neighborhood of 175,000 to 200,000 BTU's, quite a jump from 35,000-40,000 BTU's which standard tanked units demand.

A little off-topic, but most of Bosch's units use galv. Type B vent pipe, most other units from Takagi, Noritz, and Rheem require 4" Cat 3 S/S vent pipe. Bosch is actually making a line of tankless heaters that can be vented with 3" PVC which will be something to see. Hope this info helps.
Reply With Quote
  #16 (permalink)  
Old 04-15-2008, 01:23 PM
LazyPup's Avatar
Master Journeyman
 
Join Date: Apr 2004
Location: Sharon, PA, USA.
Posts: 2,133
LazyPup is on a distinguished road
There is nothing in the codes that would prevent installing a non-direct vent tankless in a basement, providing you can achieve proper venting.
Reply With Quote
  #17 (permalink)  
Old 04-17-2008, 05:47 PM
New Member
 
Join Date: Jun 2007
Posts: 3
travisdecpn is on a distinguished road
As long as it is a powered vent unit, which most tankless units are, it should pass code, sorry about the poor info. I would much prefer to have a direct-vent unit in a basement though, that's just me though.
Reply With Quote
Reply



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

vB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

» Forum Navigation
     > Forum News
     > Illustrations
     > You Gotta Laugh!
     > Catch All
     > Plumbing
     > Electrical
     > Flooring
     > Wall Coverings
     > HVAC
     > Stenciling
     > Appliances
     > Audio & Video
     > Projects
     > Faux Painting
     > Painting
     > Gardening
     > Decks & Fences
     > Outdoor Projects
     > Garage Doors
» Links

» Search

Home Repair Forum
Google   
» Online Users: 34
0 members and 34 guests
No Members online
Most users ever online was 388, 07-01-2007 at 01:54 AM.
Powered by vBadvanced CMPS v2.2.0

All times are GMT -5. The time now is 02:35 PM.


Powered by vBulletin® Version 3.6.4
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.