"Giant" hot water tank stoped working

Good day everyone,

Im stuck and do not know what els to do. Friday night my hot water tank, made by Giant 40gal 1999 stoped working.

We drained the tank, shut off the braker.
We replaced the 2 elements with 2 brand new giant elements the thermostats were replaced with new ones. We tested the wires and 120 is going to both so 240 in total. Hooked back up everything with the giant specifications. We still have no hot water. A hot water tank is just 2 elements +thermostats and a tank so if I replace everything it should work right ? the only thing i didnt replace was the tank.

I wish there was a led or a small lcd screen telling me whats not working. any help would be great
Reply With Quote
  #2 (permalink)  
Old 04-30-2008, 03:29 AM
HayZee518's Avatar
Master Journeyman
 
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 3,192
HayZee518 is on a distinguished road
Send a message via AIM to HayZee518 Send a message via Yahoo to HayZee518
check out the illustrations there is a wiring diagram for most domestic hot water heaters in there. make darn sure you got everything wired correctly. your power input should be 240 NOT 120 as you stated.
Reply With Quote
  #3 (permalink)  
Old 04-30-2008, 05:46 AM
New Member
 
Join Date: Apr 2008
Posts: 3
xilbus is on a distinguished road
Hi thanks for your reply,we bought a tester and each element is receiving 120 so that mean 240 in total or should 240 be going to each element?. I will be going back and checking up on the wirering.

The funny thing is that i just bought a house and im moving out of this one in 1 week, so now my plan is to buy a new hot water tank, set it up at the new house and bring the old one over here.
Reply With Quote
  #4 (permalink)  
Old 04-30-2008, 06:24 AM
HayZee518's Avatar
Master Journeyman
 
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 3,192
HayZee518 is on a distinguished road
Send a message via AIM to HayZee518 Send a message via Yahoo to HayZee518
the power input to the heater should be 240 volts. check the top two screws at the upper thermostat, it should read 240. if it isn't go back to your panelbox and look at the breaker(s) feeding the tank. the breaker should be a two pole breaker. sometimes two single pole units are installed with a plastic tie-bar across the two breaker's handles so if one trips it takes the other with it. if this is not the case then put in a tie-bar. across each operating element you should read 240 volts NOT the 120 you state. True, from each leg to earth ground you'll read 120 volts but the elements are meant to operate at 240 volts.
Reply With Quote
  #5 (permalink)  
Old 05-01-2008, 07:54 AM
LazyPup's Avatar
Master Journeyman
 
Join Date: Apr 2004
Location: Sharon, PA, USA.
Posts: 2,133
LazyPup is on a distinguished road
I would be curious to know where you touched your meter probes when you measured 120v?

As Hayzee has already explained in a 240 circuit both "Line1" & "Line2" of your incoming power line are powered at 120v. The bare or green earth ground wire of your incoming power cable should be connected to a green grounding screw at the point where the power cable attaches to the water heater. That grounding screw is connected to the body of the water heater to the tank will always be at ground potential.

In a water heater the top thermostat is a SPDT (single pole double throw) switch, which performs an either/or function between the top and bottom heating elements.

During cold start the upper thermostat sends the power to the bottom thermostat, which is a normally closed-open on rise thermostat. During cold start the bottom thermostat would be closed sending the power to the heating element. If you touch one probe of your meter to one terminal on the lower heating element and the other probe to the opposite terminal you should read 240v.

With 240v the heating element is on and it should be heating the water. When the water temperature reaches the preset temp on the thermostat the thermostat opens, turning the heating element off. At that point you should read zero volts on the heating element terminals, however, if you touch the red probe of your meter to either pole on the heating element and the black probe to the water heater steel tank you will read 120v. The reason here is simple. The thermostats switch "Line1" but "line2" is wired direct to the heating elements therefore if you measure from the heating element terminals to the steel tank you are measuring "line2" to earth ground, which will always be 240v.

The bottom line, if you measure the voltage across the two heating element terminals and you get zero, that element is in the off position. If you measure 240v it is in the on position.

If you are measuring across the heating element terminals and getting 120v your water heater is not wired correctly and you have both elements in series.

Last edited by LazyPup : 05-01-2008 at 07:58 AM.
Reply With Quote
  #6 (permalink)  
Old 05-01-2008, 08:45 AM
New Member
 
Join Date: Apr 2008
Posts: 3
xilbus is on a distinguished road
Hi Everyone,

Thank you for all your help. Just to update you I finally called in a ellectrician and the problem was at the main braker box. He replaced cables in there and now the hot water tank is working great. it seems that only 120 was going from the braker box to the tank. No more going to my parents for a shower lol
Reply With Quote
Reply



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

vB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

» Forum Navigation
     > Forum News
     > Illustrations
     > You Gotta Laugh!
     > Catch All
     > Plumbing
     > Electrical
     > Flooring
     > Wall Coverings
     > HVAC
     > Stenciling
     > Appliances
     > Audio & Video
     > Projects
     > Faux Painting
     > Painting
     > Gardening
     > Decks & Fences
     > Outdoor Projects
     > Garage Doors
» Links

» Search

Home Repair Forum
Google   
» Online Users: 39
0 members and 39 guests
No Members online
Most users ever online was 388, 07-01-2007 at 01:54 AM.
Powered by vBadvanced CMPS v2.2.0

All times are GMT -5. The time now is 02:38 PM.


Powered by vBulletin® Version 3.6.4
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
Search Engine Friendly URLs by vBSEO 3.1.0