Home Repair Forum



Reply
 
Thread Tools Display Modes
  #1 (permalink)  
Old 05-10-2009, 05:54 PM
New Member
 
Join Date: May 2009
Posts: 1
Thanks: 0
Thanked 0 Times in 0 Posts
MICk is on a distinguished road
New toilet plumbing

I am adding an upstairs master bath in a small room connected to the master bedroom. There is a wet-wall containing plumbing for an existing upstairs bath and existing downstairs bath. The existing upstairs and downstairs toilets each have their own wastepipes to the main drain in the crawlspace. Can a new toilet connection be added to the vented vertical wastewater pipe that serves the downstaires toilet or would this be a no-no? If not, can a 2-way toilet arrangement (one on each side of the wet-wall) be installed on the vented upstairs vertical wastepipe?
Reply With Quote
  #2 (permalink)  
Old 05-11-2009, 01:22 AM
Redwood's Avatar
Handyman
 
Join Date: Feb 2009
Location: Connecticut
Posts: 156
Thanks: 10
Thanked 15 Times in 14 Posts
Redwood will become famous soon enough
You may not wet vent between floors.
If that pipe serves as a vent for the first floor toilet you cannot use it.
__________________
I stayed at a Holiday Inn Express last night.
Now I can Plumb!
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.


For great information on the history of sanitary sewers including the use of Redwood Pipe
Visit
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.
Did you know some Redwood Pipe is still in service today.
Reply With Quote
  #3 (permalink)  
Old 05-14-2009, 06:24 PM
New Member
 
Join Date: May 2009
Posts: 10
Thanks: 0
Thanked 0 Times in 0 Posts
devidmike is on a distinguished road
If you want to stay compliant to your building codes, no. If you don't care about code violations (may be an issue if you ever sell your house) then go ahead, it will work just fine. Just remember the plumbers 3 important rules: Brown trout don't swim upstream, don't bite your fingernails and payday is on Friday.
Reply With Quote
  #4 (permalink)  
Old 05-14-2009, 08:52 PM
Handyman
 
Join Date: Feb 2008
Location: Evansville, In
Posts: 167
Thanks: 2
Thanked 16 Times in 16 Posts
jnaas2 is an unknown quantity at this point
Send a message via AIM to jnaas2
There is a reason as redwood stated that you dont use a vent for fixtures upstairs and one of them is when you flush the toilet upstairs it will more then likely pull or push air in or out of a fixture downstairs which will lead to sewer gas in you house. There is a reason for all the codes and as stated you dont need to follow them if you are not having it inspected but its sometimes easier to do it right the first time verses doing it again, the choice is yours
Reply With Quote
Reply

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Stats
Members: 12,842
Threads: 7,748
Posts: 33,127
Top Poster: HayZee518 (4,918)
Welcome to our newest member, nerbonne
» Online Users: 38
0 members and 38 guests
No Members online
Most users ever online was 400, 06-22-2009 at 07:11 AM.
» Links

» Sponsors
Powered by vBadvanced CMPS v3.0.1

All times are GMT -5. The time now is 08:56 PM.


Powered by vBulletin® Version 3.8.4
Copyright ©2000 - 2009, Jelsoft Enterprises Ltd.
Search Engine Friendly URLs by vBSEO 3.3.0