    breakers manufactured these days are Cu-Al rated. any good anti-oxidant used with aluminum will work. 6/3 with ground copper romex will work with a 65 amp breaker, 6/3 aluminum will work with a 50 amp breaker.

  2. #12
    Join Date
    Apr 2011
    Posts
    6
    Thanks {vb:rawphrase post_thanks_given 
    1
    Thanks Thanks Received 
    0
    Thanked in
    0 Posts

    Ground Wire Size

    One more quick question, did I hear that my ground wire must be the same size because this is for a subpanel? Or can I use a 6/3 Romex with a smaller bare ground wire (8 or 10) for the 50A subpanel?

    Thanks again,
    Joe

  3. #13
    Join Date
    Jul 2004
    Location
    Saint Regis Falls, NY, USA.
    Posts
    8,743
    Thanks {vb:rawphrase post_thanks_given 
    1
    Thanks Thanks Received 
    487
    Thanked in
    470 Posts
    6/3 romex has a reduced size earth ground. It attaches to an auxillary ground bar that you buy for the panel. The neutral is full sized and connects to the neutral bus with no bonding screw.