Monitor 422 lights then cuts out
  • Monitor 422 lights then cuts out
    Hello, My Monitor 422 will turn on and I can see the flame. The burner status lights up with 4-5 bars then the flame stops and in a minute or 2 the burner status lights blink. I have cleaned the filter in the unit, installed a rebuild kit with new gaskets and blew out and cleaned the soot out of the exhaust pipe. If anyone has ideas I would be very appreciative. Thanks
    M422
    Short of having an air lock in your line; or being low on fuel; I would say the flame sensor is touching the ring or burner.
      Thanks for the info. The only way I could replace the sensor was to point it upwards. Is that correct? Should it point down?
        M422 overhaul
        It should point downward. The problem comes if the angle is off and the sensor touches the ring or the edge of the pot. What did you use for a flame sensor gasket? You stated you did an overhaul. Could you go over all the stuff you did and which parts you replaced?
          flame rod
          with the flame rod in place and the gasket applied you can move the flame rod side by side by loosening one screw and tightening the other. it needent be reefed on down, just enough to afford a seal against the kero fumes in the pot. the metal of the flame rod is nickel silver, very hard and very brittle.
            Monitor works now
            Thanks Guys, I reversed the direction on the sensor and it came right up to temp. and now we are warm. Thanks for the good advice.
