    What is a good reasonable priced accurate manometer to measure my barometric damper?
    My furnace should be 0.025 and my flue should be -0.02. Looking at the gauges for sale i see accuracy (read
    inaccuracy) ratings that would make readings in the range that I need almost useless. Exp:
    0.3% of full scale 55.00wc (0.003x55=0.165) Does that mean that a reading of 0.02 could be off by as much as
    0.165?
    +/-0.3% of full scale 83.02 InH2O NKTECH NK-L3 (0.003x83.02=0.249)
    1.5% of full scale 4.00wc Dwyer 478A-0 (0.15x4=0.6)
    Am I doing something wrong here?
    tks,
    pa
  2. #2
    Join Date
    Aug 2008
    Location
    Bridgton, ME
    Posts
    136
    Thanks
    0
    You're on the right track, except +/-1.5% = 0.015 x 4" = 0.06" wc. I suggest you look at instruments with a full scale deflection closer to what you are trying to measure. For instance, a Dyer Magnehelic 2000-0 with a full scale of 0.50" wc & and an accuracy of +/-3% FS has an error of .03 x .5 = 0.015". I bought one of these on eBay a while back for $35. Also, Dyer will calibrate their instruments for a fee.
  3. #3
    Join Date
    May 2010
    Posts
    17
    Thanks
    0
    great tip. that would be more accurate. I asked dwyer and they just suggested their 400$ digital high range unit that was not any more accurate. I hope their gauges are better then their customer service.
    On their Magnehelic 2000 page i also see one that is 0.25-0-0.25" w.c. and another that is 0.125-0-0.125" w.c.