    troubleshoot gas wall heater- thermostat? wire?

    Hi, I have a older (15+years) cozy direct vent gas wall heater with the original manual thermostat wall control (2 wire).

    Last year, the gas valve was replaced after replacing multiple thermopiles ( pilot would go out).

    Its been working fine until last week- the pilot stays on but the gas valve doesn't "open" unless I give the valve a little whack. then the gas valve will be responsive to the thermostat for a bit then non responsive after.

    I tested the thermostat with a jumper cable- no response
    I tested the TH TH/TP on the gas valve with a jumper cable- fired up and then right after tested the thermostat- it fired up.

    Is the issue a faulty gas valve, faulty wire or thermostat?

    I hope the issue isn't the gas valve it was expensive to replace.

  2. #2
    Join Date
    Jan 2014
    Posts
    139
    Thanks {vb:rawphrase post_thanks_given 
    4
    Thanks Thanks Received 
    13
    Thanked in
    12 Posts
    Clean all connections to bright metal including the wires, clean thermocouple base in the gas valve and reseat it.