    I'm hooking up a designated line for my frige. I was thinking of using 12-2 wire with a 20 amp breaker. Is the 20 amp breaker over kill or should I use the 12-2 with a 15 amp breaker

  • #2
    For a refer you can use a dedicated 15A circuit using #14 wire or a 20A circuit using #12 wire.

    I see you have several posts asking similar things. The breaker protects the circuit, NOT the appliance. So there is NO reason to undersize the breaker.

    Comment


    • #3
      Amperage

      Thanks for the tips.

      Comment


      • #4
        dedicated circuits for a dwelling:
        dining room circuit 20 amp. kitchen countertops - one 20 amp per three receptacles. refrigerator - one dedicated 20. disposal and dishwasher can share one 20 amp circuit. island if you have one - one 20 amp circuit. microwave - one 20 amp. lighting can be on a 15. clock hanger - one 15 shared. range igniter can share a circuit off the lighting.

        Comment


        • #5
          Originally posted by HayZee518 View Post
          dedicated circuits for a dwelling:
          dining room circuit 20 amp. kitchen countertops - one 20 amp per three receptacles. refrigerator - one dedicated 20. disposal and dishwasher can share one 20 amp circuit. island if you have one - one 20 amp circuit. microwave - one 20 amp. lighting can be on a 15. clock hanger - one 15 shared. range igniter can share a circuit off the lighting.
          Most of these are generally rules-of-thumb and not code requirements.